main bonding to external boiler. | Page 2 | on ElectriciansForums

Discuss main bonding to external boiler. in the Australia area at ElectriciansForums.net

S

sparkygg

This is my first post and hoping someone can help?

Just wired an external combi oil boiler. I ran a 10mm bond from CU to the incoming pipes which are all 22mm and 28mm copper. They come through the wall from outside and I have put an earth bonding clamp on each pipe and looped the bond between them all. Now I am not sure if I should have run the bond out to the oil line entering the boiler? It comes through the ground for 20m or so and pops up just beside the boiler which is mounted on a paving slab plinth. The oil pipe doesn't enter the building and as i said any metal pipes which do are now bonded. The incoming water is in blue polypipe and is bonded where it turns to copper further into the installation. What should I have bonded? I am confused!

Any guidance would be appreciated.
 
Wirepuller is correct - your equipotential zone is within the house, you do not want to make it any bigger, or you can get to the stage where you put a potential where there is no need for one.
It is always correct to bond at point of entry to the building(s) and if it does not come into to the building leave it alone.
 
I'll take issue with this.
It is not possible to have an 'equipotential zone ' in an external situation...(such as surrounding an external boiler).....in such a situation the boiler is surrounded by the general mass of earth so it would be pointless trying to create an equipotential zone by bonding the oil line.
The equipotential zone is in the building , and the heating pipes coming from the boiler introduce an earth potential...(possibly from the oil line)....therefore it is correct to main bond the heating points at the point of entry.

Maybe i didn't read the OP's post too well!! lol!! I was under the impression that the boiler was situated/located within an external outbuilding of some kind, or even an outside cupboard type affair that is within the house boundaries but only accessible externally. Can't say i've ever seen an outside/externally mounted combi boiler, so never considered such an installation.

So if this is indeed the case, Yes your correct in what your saying above...
 
To my mind, if the oil pipe is considered an extraneous-conductive-part, it will require bonding.
If the boiler is within the building, the oil pipe will require bonding as close as practicable to where it enters the building, preferably within 600mm.
If the boiler is in another building, then it may be that it should be treated as a separate installation, and will require it's own earthing and bonding arrangements (i.e. TT).
In any event the oil pipe should be bonded.

I disagree......if it's in an external situation it is impossible to create an equipotential zone,thats the whole point of bonding. If the boiler is completely external the potential from an oil line will be introduced to the equipotential zone via the heating flow/return....they will need bonding at the point of entry to the building.

@E54.......external stand-alone boilers are quite common around here...and I always bond incoming pipes at the point of entry to the building.
 
@E54.......external stand-alone boilers are quite common around here...and I always bond incoming pipes at the point of entry to the building.

That's fine wirepuller, it's just that i've personally never seen them, so didn't consider such an installation/situation in my reply/post!! I would still earth any metal oil tank and/or pipes though, if only for tanker equalisation filling purposes.
 
ERRRHHH NO - The tanker will if necessary earth to the tank , how ever if you have earth leakage (parallel paths and all that) from any electronic equipment or a low fault you will be putting a potential into the tank which may or may not cause a problem.
 
Every filling station, commercial or private that i have been involved with (and their have been many) had the fuel tanks earthed via Rod mat or other form of electrodes connected to both the tanks and a common reel lead position ( a statutory requirement in most of the countries i've worked within).

Because the reel lead is connected between the tanker and the underground tanks first, before any filling pipes are connected, both the tanker and tanks will be at the same potential!! It doesn't matter if the reel lead is mounted on the tanker or the installation being filled...
 
Last edited by a moderator:
Not really relevant in this situation but every tanker discharge/loading point I’ve dealt with would have the static equalisation point fitted. In our case we were dealing with granulated or powdered product. Where the danger is after the pipe is connected and the product is travelling through causing some nasty static build up.
 

Reply to main bonding to external boiler. in the Australia area at ElectriciansForums.net

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
I
  • Article
Water hammer/noise from pipework at night? I attended a Job where the customers complained about noisy pipes more often late at night bur...
Replies
0
Views
180
Illuminate
I

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top