Hi all,
New to this forum so I'll introduce myself as an electrician working for an NIC approved contractor in Sussex.
Last week I did a PIR on a church and the only defect was a lack of main bonding to the lightning conductor. Bs 7671 lists this as a requirement but I cannot see why it is necessary, given that said lightning conductor is on the outside of the building and so outside of the equipotential zone. Also it seems to me that a bond on to the lightning conductor will simply 'import' a lightning strike into the electrical installation.
The NIC technical guide states that while a bond is required , the complexities of other british standards involved means that it should only be undertaken after consulting a L/C specialist,and should be listed as a code 3 on the PIR. If anyone can enlighten me on why bonding L/C's is a good idea I would be grateful
Cheer's ...Alan
New to this forum so I'll introduce myself as an electrician working for an NIC approved contractor in Sussex.
Last week I did a PIR on a church and the only defect was a lack of main bonding to the lightning conductor. Bs 7671 lists this as a requirement but I cannot see why it is necessary, given that said lightning conductor is on the outside of the building and so outside of the equipotential zone. Also it seems to me that a bond on to the lightning conductor will simply 'import' a lightning strike into the electrical installation.
The NIC technical guide states that while a bond is required , the complexities of other british standards involved means that it should only be undertaken after consulting a L/C specialist,and should be listed as a code 3 on the PIR. If anyone can enlighten me on why bonding L/C's is a good idea I would be grateful
Cheer's ...Alan