Hi all,
just took main protective bond (10 mm) to water pipe which is of the old lead type.
Main bond length is about 4 meters.
Cross bonded to rads and sink(utility sink)
Then did R2(using 2.5mm) to pipes under the kitch sink.
Reading was 0.10 ohms.
regs say max allowed value is 0.05.
This reading seems a bit high.Anyone got any reasons for this(plumbers joints,lead pipe,or 2.5 R2 lead) and would it be acceptable.
Need to know as Napit assessment is due on the start of June...............