N

Nicktric

Hi I am doing a CU change and have 10mm gas bond direct to the MET. There is no conductor back to the MET for water but it is bonded in 10mm and there is continuity back to MET. I know this is acceptable if the conductor is not cut but I know it is, should I run a new 10mm conductor from incoming water to MET or just note it in departures?
Thanks
 
Assume you are saying that the water is linked from the gas but not continuous?....if so use a crimp lug large enough to take both 10mm cables at the gas, a 25mm lug will do it. Ensure both cables are securely crimped into the same lug,this will meet the requirements.
 
Thanks WP.The gas is a a recent install and a single 10mm back to the MET. The water has no bond back to the MET but I can see 10mm at the entrance to the property. When I disconnect the 10mm at the stop tap I get good continuity back to the MET but I can't see where it loops to the gas. There is no supplementary bonding. I am sure it is not continuous as the gas is quite recent. So unfortunately can't join them..? So in that case is it a new run? Also this one will be assessed..
Thanks.
 
So it must be joined somewhere as you have confirmed continuity of the conductor. Out of interest what was the reading of the conductor?

As it is an assement, personally I would run another bond for the water, on assessments the more you do it "to the book" the better, in real life ...............hmmmmmmmmmmmm not saying;):D
 
No Telectrix it isn't. 0.45ohms Malcolm, thanks and feel as though I should run another to save even having the discussion on the day..!
 
oops, meaqnt 500 yards. typo'd , sausage fingers. LOL. anywat, no smarter than your next town comment.
 
book is in van.
info time: 4 rods = 1 chain (22yds): 10 chains = 1 furlong, 1 acre = 1 furlong x 1 chain. thats 1 horse and 1 man ploughing for a day.
 

Reply to Main bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
608
loz2754
L

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top