Does the building have a steel structure if so bond to that, as long as the steel is bonded back at the MET which it should be anyway!
The building is structural steel, sheeting rails and cladding,,, I noticed it on a job I looked at last week, the origin isn't that far away were there is a suitable MET and section board, however the contractor has decided to bond steel, water and gas from a sub DB, the sub main is a 16mm SWA cable, using the SWA as the earth.. It interested me as I have never seen that done before, I can see that they have done it because the incoming supplies were close to the DB but I was unsure wether this is acceptable??
 
The building is structural steel, sheeting rails and cladding,,, I noticed it on a job I looked at last week, the origin isn't that far away were there is a suitable MET and section board, however the contractor has decided to bond steel, water and gas from a sub DB, the sub main is a 16mm SWA cable, using the SWA as the earth.. It interested me as I have never seen that done before, I can see that they have done it because the incoming supplies were close to the DB but I was unsure wether this is acceptable??

Using the 16mm SWA as a main earth bonding conductor is NOT acceptable, it will not have an appropriate copper equivalent CSA. The steel wire armouring is fine for use as a CPC but not where protective main earth bonding requirements are also to be met!!
 
Tony mc hit the nail on the head, once that structural steel is bonded, you've got a rather large main protective bonding conductor to 'tap off' to bond other services.
 
Using the 16mm SWA as a main earth bonding conductor is NOT acceptable, it will not have an appropriate copper equivalent CSA. The steel wire armouring is fine for use as a CPC but not where protective main earth bonding requirements are also to be met!!
Thanks engineer 54, I thought as much, seeing things like this makes you think somebody knows something more than you. I didn't want to point it out as incorrect and look stupid if there was a way of doing it that way. Is there a calculation to use to determine the size it must be?? Let's say the sub main was a 150mm SWA cable, would it then be sufficient ? I would always say it has to come from the origin, but surely there will be some kind of calculation that would determine if it was safe. Thanks again, Iam just trying to understand it a bit further as you do :)
 
Generally it is not recommended to use the armouring of SWA as a bonding conductor, especially where the supply is TNCS as there can be currents circulating through the bonding due to the design of the PME system that may have adverse effects on the current carrying capacity of the cable as a whole.

The comparative calculation for steel versus copper as a conductor is that the steel must have a cross sectional area of 8.5 times that of the copper because the steel is less conductive.
This would mean that where a 16mm² copper bonding conductor is in use then a steel conductor would need to be 136mm² to afford the same protection.

16mm² SWA armour has a CSA of 45mm² which is approximately equivalent to 5mm² in copper so unsuitable for any bonding conductor, even is it were an acceptable use of the armour.
 

Reply to main bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
790
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top