robbie t

why would a suppliers main cut out fuse an old type 60 / 80 blow . just installed a socket i isolated the whole fuse board added a new socket spur off the ring ,tested R1 -R2 and insulation resistance all expected values .turned main isolater back on at the fuse board and there was no power ....... any idears
 
It happens sometimes if you don't progressively switch all the loads back on, especially if its an ancient old fuse. I would imagine its happened to all of us, well to me at least, usually at about five to five on a Friday! Hmm decision time, do I cut the seal and replace it, or do I call out the DNO and wait four hours?
 
Possible main switch issue, large power surge when turning back on (unlikely though) or you really f****d up somewhere! :rolleyes: Guaranteed if it were the last one you would be able to find the fault without the need for a test meter, the scorch marks and smell of burning would be the easy bit to find! ;)
 
no banging sound was heard no power to digital suppliers meter so checked continuity across cut out fuse as safty tags already being remove and fuse had blown was only a one bedroom flat not occupied no load drawn when turning main switch back on . can cut out fuses deteriate ?
 
.

hope you pulled the fuse before doing the continuity check...tired fuses can just fail when you switch a load on to them. if the seal is missing and you have a spare fuse, bung it in ( observing all safety precautions, no load on installation when you put the fuse in, etc. )
 
Last edited:
one doesnt have a spare fuse lol why on a friday afternoon lol:party:

you must have a 2" nail floating about in your kit, surely.

oops, for a moment, thought you were a kitchen fitter.
 
have found loads in industrial installations, just failed, no signs of overload.just old and tired. bit like me after 40 years in the trade, won't take much to finish me off. LOL.
 
im only just starting and i have enough already lol why does a simple job turn in to a bitch i dont mind on a monday morning dont get me wrong lol not when its pub time lol ............ thanks for comments
 

Reply to main cut out blowing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top