Folks need advice. House I am working on. TT earthing. The rod is closer to the gas pipe/meter box than the Consumer Unit. I wondered why I could find no bonding conductor in the CU. It appears someone took the Main Earth 16mm cable from the earth rod to the gas pipe and then onto the Consumer Unit. The cable is not broken and continuous. II can't see this being correct but can't establish where in Regs it's not compliant. Maybe I am too fussy as I like to see bonding conductor's on the MET not going hunting for them. Am I right, if so where in Regs?
 
542.4 Main earthing terminals or bars.
542.4.2 "To facilitate measurement of the resistance of the earthing arrangements, means shall be provided in an accessible position for disconnecting the earthing conductor..."

To my mind, having the gas bonding incorporated in the earthing conductor does not provide for this regulation to be fulfilled, as disconnecting the earthing conductor at the DB would not disconnect it from the gas pipe, leading to erroneous measurements.
 
542.4 Main earthing terminals or bars.
542.4.2 "To facilitate measurement of the resistance of the earthing arrangements, means shall be provided in an accessible position for disconnecting the earthing conductor..."

To my mind, having the gas bonding incorporated in the earthing conductor does not provide for this regulation to be fulfilled, as disconnecting the earthing conductor at the DB would not disconnect it from the gas pipe, leading to erroneous measurements.
Excellent and prompt reply. Are you quoting this from recall 😂 If so I am impressed. Yes it did not feel right to be honest and often my gut reaction has been right.. Maybe I should rely on that a bit more. Obviously this has been done by the gas Installler a few years ago. I had looked through section 5 of the Regs but sometimes I find interpretation is everything. Totally agree with your assessment and will help greatly. Thankyou
 
One of these between the earth rod and gas main would allow disconnection from the CU and gas pipe: barrette de mesure terre - Recherche Google - https://www.google.com/search?

[ElectriciansForums.net] Main Earth and Gas Bond

Is having to disconnect inside the DB an accessible position?
 
Last edited:
Surely it's easy enough to just drop the wire off the clamp on the gas pipe during testing ?
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would pick up on this and just do what you said, but it seems against the intent of the reg quoted to have 2 things to disconnect.
 

Reply to Main Earth and Gas Bond in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I like your way of thinking.
Replies
6
Views
475
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
Replies
23
Views
2K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
475

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks