Does the main earth bonds i.e.. Water , gas, oil have to go to 'MET' at suppliers cutout next to meter or in consumer unit suffice. What about a comercial premesis where you have sever sub boards can it come off the nearest db?
 
I'd agree with Badged, although where possible I always connect the main bonds to the same place as the main earthing conductor, i.e. the MET. On larger installations I can see where it would be more practical to connect main bonds to a closer EMT. But don't do it out of laziness of to save a bit of cable!
 
So aslong as the sub main feeding the sub boards is >10mm conductor and labelled correctly this would be ok from a sub board?


On large commercial and many industrial installations, bonding cable sizes could well exceed 10mm.

Generally nothing wrong connecting locally bonded metalwork etc to the EMT of a sub-main DB. In fact it would be crazy to take every bonding connection directly back to the installations MET. In many instances the frame of the building will be steel/iron, Once this steel framework has been solidly bonded to the installations MET, connections to other extraneous services etc, can be effectively bonded to the buildings steel framework.
 

Reply to main earth bond.. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top