if the TNS supply has the old blck earthing conductor connecting to the MET looks like 4mm2 can we connect to that clamp with a new bit of 16mm2 or is this down to the DNO? im on about the original clamps with the soldered connection.
the reason i ask is because i did a board change and it had the old black 4mm2 and i crimped a lug ont the 16mm2 and connected it to the clamp on the tns earth sheath in addition to the existing earthing conductor. hope this makes sense!
I'd just put an MET there with the existing 4mm from the lead sheath going into it. Then whack ur 16mm from ur consumer unit into that MET. Dont touch their stuff I say .