Hello All,
Tying my brain in knots trying to work out if this earth is ok:
TT system with 100mA RCD on tails
Tails then go into an isolator with 60A BS1361 fuse which supplies nearby consumer unit and a remote consumer unit in next room.
Remote consumer unit is supplied via twin and earth 10mm (so 4mm CPC - am I right?)
So applying the adiabatic equation to this, my problem is:
Earth rod resistance is 4.05ohm and PFC (to earth) 56A....therefore my 60A fuse is never going to blow so I can't get a 'time' number for the equation.
Obviously the 100mA RCD would trip in the event of an earth fault, but it isn't an RCBO so isn't listed in appendix 3 (time current characteristics) so I'm not sure what to do!
Any help much appreciated