Hi all, regards the csa of the earth to a sub main in a flat, does it need to me 6mm or 10mm or larger still? There is a flat with PME and they have asked for an EICR. However, the sub main is fed via 10mm t&e and the earth is only 6mm with a 10mm supplementary bonding and 10mm to gas reliant on this. The 10mm to water goes directly to the MET at the incoming main. Would this be a C2 or C3? Got a Ze of 0.21. I would have thought with the Adiabatic equation that it would suffice but not with selection based on the tables.
It states a C2 on the electrical safety council best practice guide [FONT="]"Cross-sectional area of the earthing conductor does not satisfy adiabatic requirments (that is does not comply with regulation 543.1.1)[/FONT]
Yet, regulation 543.1.1 seems to say it can either be calculated or selected?? There is a 60amp BS 1361 at isolator. Gona be a pig to run a new earth cable if required as in a communual area and a fair way.
Many thanks
It states a C2 on the electrical safety council best practice guide [FONT="]"Cross-sectional area of the earthing conductor does not satisfy adiabatic requirments (that is does not comply with regulation 543.1.1)[/FONT]
Yet, regulation 543.1.1 seems to say it can either be calculated or selected?? There is a 60amp BS 1361 at isolator. Gona be a pig to run a new earth cable if required as in a communual area and a fair way.