Main Earthing Clamps | on ElectriciansForums
Discuss Main Earthing Clamps in the Australia area at ElectriciansForums.net
L
Ladders
Hi. Once again I go to a property and find the 16mm earth to the TNS system head is on a standard 'sparky' earth clamp.
Problem is. The client wants me to change all the fittings to metal ones. So as the main earth is not correct I presume I can't? Will the client have to pay the board to fit the correct type of clamp first before any work takes place?
No sign of the orginal earth strap anywhere plus the installation does not comply like this anyway!
I'd first try to contact the DNO for the area and see if they will maintain (ie fix) the existing TNS system, that would be free. To install TNCS(PME) would most likely cost the home owner of the order of ÂŁ150.
So what's the Ze on this cable sheath?? If it's under 0.8 ohm then it's most definitly a TN-S supply. If that's the case, why not just replace this standard clamp, with a couple of constant tension spring clamps and appropriate braid tail?? I certainly would!!
Would the supplier be responsible for the main earthing? Could they keep it on a tn-s and put their own clamp on mechelec?
It sounds in your case that there was no earth supplied to the property. If they had supplied an earth it wuld have been either a hepbond (braid clamped to lead) fitted or a simple copper wrap (several turns of single uninsulated copper wrapped around the lead) usually under pitch impregnated cloth tape. If the above is correct then they would charge the same for either PME or TNS earth terminal as effectively the main job is providing a hepbond to the cable and a henly block. The only difference is a link between neutral and earth terminal (PME).
That said if the cutout was damaged then they would come out and repair within 4 hours and if available PME it at the same time.
Reply to Main Earthing Clamps in the Australia area at ElectriciansForums.net
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic