When installing new CCU its a must to have 16mm earth and 25mm tails,yes ? Otherwise dont install is what i've been told.
What about main equipotential bonding to gas and water and maybe others like oil ? It should be 10mm but supposing its not practical to get to it without considerable expense/disruption ? Could this be left as code 4 ?

Also,many houses will have some kind of bond to earth on the water but maybe only 4/6mm
could that be left as code 4.Thanks.
 
you would probably find that 6mm bonding to gas/water is capable of carrying the PFC so, as long as it's securely connected, and gives a good continuity reading, if it's a ballache to replace, then i would give it a code 4.
 

Reply to Main Equip' Bonding & New CCU in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
661
loz2754
L
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top