I over looked a job today and I saw a situation that had me thinking...
Basically it was a 6 way consumer unit that was about 15 years old and has a BS 4293 100A RCD fitted. Now the main service fuse was rated at 60A i think. Now what can be done in this situation...
The consumer unit needs to stay but what can be done with the main service fuse, can this be changed for a 100A by the supplier or should the RCD be changed as these large RCD's are obsolete now??:confused:
 
It was because the chap doing the work commented on divesrity and that 100 Amp RCD should have a smaller max current rating to the main service fuse. Is this not required? the reason why the unit needed to stay was purely down the the size and location. The final circuits had no leeway on length and changing it could mean extending all the end's of the cicuits. The maximum demand checked out fine.
 
I think this chap needs to refine his knowledge as the rcd 100a rating is what it can operate up to and not a overload tripping rating, rcd gives earth leakage protection only and as long as its ampage ratinge is greater or equal to the fuse upstream then its ok.
This chap is probably getting confused with a rcbo where in this case the 100amp would be the overload rating and thus a comparison for the rcbo and hrc fuse tripping/current curves will show which device would open first, in a short circuit situe the smaller device downstream usually gives discrimination against the incomming fuse and only a short in the tails should effect this fuse unless the demand of the installation exceeds 60amps for a long period of time due to the accumulative loads on each mcb.
 
Yes, it was something that had me thinking as I'd not come aross this before and like you say it would only be a short very close to the main that would create any real issue. Thankyou for setting me staright on this.:rolleyes:
 

Reply to Main fuse and rcd issue in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...
Replies
5
Views
994
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top