on my installation the consumer unit is protected by a BS 88 fuse 100a, i was just looking in the on site guide and it says the rated short circuit capacity is 50 at 415 v.. when doing my PSC i got 1.6 ka and PEFC of 1.4ka does this mean my main fuse is to low to deal with possible prospective fault current?