Farmelectrics

-
Arms
Joined
Nov 9, 2010
Messages
3,057
Reaction score
520
Location
Wirral
Just sitting down for tea and door bell goes neighbour tells me his main fuse is hot to touch and a smell of burning is present goes across and he's right burning smell and very warm main fuse so isolates consumer looking for any burning or loose cables in consumer all ok fuse is sealed but seems a bit loose he doesn't want me to cut seal to check as he's waiting for dno to come out anyone had similar please tell me ha ha don't want him knocking back when the footy starts
 
Id avoid wiggling the tails if the service fuse is hot its highly likely the housing holding the terminal clamps have lost their structural integrity and will just fall apart this could in a worse case scenario be extremely dangerous.
As you have already done -switch off all power and contact the supplier. I have seen these guys open up such a cutout with extreme caution and PPE to suit with tales of it may collapse and explode in your face.

If you think about the heat thats generated will travel through the fuse and overheat the insulation on the incoming cable to a point it may fail and short out at the slightest movement.:shocked3:
 
had it on a job before , 3 phase supply , fuses where to hot to touch checked everything out , clamp metered tails was not overloaded pulled the fuses and installed new fuse carriers , few days later happened again , DNO came out and changed the head no explanation worked fine after that . ( quite enjoyed watching the guys change the cable head live )
 

Reply to Main fuse hot in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top