hello guys

I need some advice on and EICR job.
On the MET we have two main bonding conductors 10mm each.
Water is fine however I cannot find the gas bond connection on the pipe.
I know it is connected to the pipe as a long lead test gives me 0.02.
The pipes resistance rises as I disconnect the main bond and clamp between the met and gas pipe.
What would you guys advise as I cannot see the connection within 600mm of the Pipe.
Code 3 advise having the bond reinstalled?
 
Did you disconnect both ends i.e. From the MET as well?
If still connected you may pick up parallel paths from say a cpc connected to the boiler through the gas pipe from the central heating circuit for example.

Sorry re read it yes you did! o_O
 
That would make the overall assessment unsatisfactory.
I'm not sure it deserves that.
The way I view it is if you're there to do an EICR, you're not there to tear the house apart to do so, in all probability you've given them a fixed price for the EICR which would cover basic, reasonable, investigative actions you'd need to take in order to complete the EICR. If you can't because of e.g. this situation then it comes under additional work/cost required and is explained/justified by the FI code.
 

Reply to Main gas bond connected in the wrong place in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
665
loz2754
L
M
  • Article
What is causing water hammer in my flat? Hello I wonder can anyone shed any light on what is becoming an annoying problem? I had a new stopcock...
Replies
0
Views
115
Mr Gwent
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top