A

Adz

Hi,

Recently i carried out a periodic inspection report. It was on a house that had a separate boiler house. The boiler house had a light, a few spurs for the boiler and heating pump. It was an oil fired boiler and i placed a defect on the report as the incoming metal oil supply pipe had no main protective bonding conductor to it. Am I right to defect this? One of my bosses said it wasnt necessary to defect it as "it was a separate building" however i still disagree. What do you think ? :confused:
 
seperate building = seperate supply = seperate test

if the oil supply pipe goes into the house it should have a bonding conductor run from within 600mm of entering the house and running directly back to the CU or MET

from the point of entry into the house is your concern, this is the equipotential zone in theory. but in your circumstance i would say that if the sockets are supplied from the house therefore they are a part of your inspection ande the CPC extends the equipotential zone and the tank should be bonded as it has the potential to become live under fault conditions.

the code 4 is a personal decision, you being the competent person are the duty holder throught the test/inspection

is there an earth spike on the tank or any of the supporting framework? if not i honestly think you'd be justified to add it as a code 1, bonding conductors are a neccessity, end of!
 

Reply to Main protective bonding conductor help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
661
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top