I've gone around in circles several times on this and I'm still not completely sure what the answer is ... generally speaking, when changing a domestic CU in a house that has a TN-S supply and 6mm[SUP]2[/SUP] main bonding (which is in good condition) is it necessary to upgrade the main bonding to 10mm[SUP]2[/SUP]?

I know that 544.1.1 says that, for non PME supplies, main protective bonding conductors must have a cross-sectional area of not less than half that required for the earthing conductor (and not less than 6mm[SUP]2[/SUP]), and 543.1.1 says that the required cross-section area for the earthing conductor may be calculated (using the adiabatic equation) or selected according to 543.1.4.

If you select according to 543.1.4 you basically end up with a 16mm earthing conductor and 10mm main bonding conductors, but if you calculate using the adiabatic equation and measured prospective fault current then I think that the required earthing conductor normally ends up being less than 12mm, meaning that 6mm main bonding is ok.

What I am a little concerned about is that the On-Site Guide section 4.4 states that the minimum csa for main bonding conductors (for 16mm[SUP]2[/SUP] or 25mm[SUP]2[/SUP] tails) is 10mm[SUP]2[/SUP]. It doesn't say, as far as I can see, that a smaller csa can be used in any situation, it just states that 10mm[SUP]2[/SUP] is the minimum. Am I right in thinking that Table 4.4 in the OSG is just based on 543.1.4 and/or is intended to give a minimum csa that will be suitable for any installation that falls within the scope of the OSG (section 1.1), i.e. worst case minimum (if so I wish that they would make that clear in the notes rather than stating that the values are minimums)

So what I really want to get to the bottom of is ... is it acceptable to size the earthing conductor and main bonding conductors according to measured Ze/PFC (for existing installations), is it ok to disregard the "minimum csa" stated in section 4.4 of the OSG when calculating using the adiabatic equation, and if so what is the justification for this, and basically is it generally ok to leave 6mm main bonding in place on TN-S installations when changing the CU?

Also, has anyone here talked to any of the Part P scheme providers about this and got their view on it?
 
There are a number of areas where the OSG and the Regulations differ.
I don't know why this is.
I would ignore the recommendations in the OSG, some of which if followed would actually result in non-compliance with BS7671.
 
Thanks guys.

So I'm thinking that if the existing 6mm main bonding has been in place for a long time, is in good condition, is correctly installed and the supply is TN-S and the measured PFC is not huge, i.e. the adiabatic equation gives an earthing conductor of no bigger than 12mm[SUP]2[/SUP], then the 6mm main bonding can be considered "adequate" and doesn't need to be upgraded.

Does that sound reasonable? Anyone disagree with that?

I'd be interested to know what everyone else generally does in this situation.
 

Reply to Main Protective Bonding (Domestic CU Change, TN-S supply) in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...
Replies
3
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top