Hi,can anyone give me some advice,i have installed a sub consumer unit which is fed from main cu using 6mm t&e.i have realised that the earth bonding should be 4 mm and not the 2.5mm.from the main board(earth terminal block) is a main protective bonding to the water main (10mm) which passes right past my sub board.my question is can i divert to my sub cu and then to the water main or is this a no no
 
Hi,can anyone give me some advice,i have installed a sub consumer unit which is fed from main cu using 6mm t&e.i have realised that the earth bonding should be 4 mm and not the 2.5mm.from the main board(earth terminal block) is a main protective bonding to the water main (10mm) which passes right past my sub board.my question is can i divert to my sub cu and then to the water main or is this a no no


Yes you could, but I don't see why you would want to.

The 2.5mm isn't 'earth bonding', as you call it.

It's a CPC for your CU sub-main circuit -

the only time it would need to be 10mm is if you were using it as both a CPC and Protective Bonding conductor (i.e. using the earth terminal in your sub CU for bonding to)

Where is the sub CU located?
 
Thanks for that,the sub cu is situated at the end of the house approx 7m and will supply a new kitchen and shower room.the existing is on the only ring in the house so i wanted to have a seperate ciruits so i will run a single 6mm t&e t to the new cu and then supply new circuits to that.i was under impression that the 6mm was distribution circuit and earth should be no less than half the line conductors ie 4mmm
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main protective bonding
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
waynelester,
Last reply from
waynelester,
Replies
2
Views
1,797

Advert

Back
Top