foghorn

HI ALL
whilst completing certificate on pirform having installed a shower consumer unit with a 40A 30ma rcd and mcb
nominal current rating of main switch in relation to overcurrent protective device (ie) main switch is rated aty a lesser value than main over current protective device, supply characteristics 100 amp bs1361

any ideas how to get round this
 
less than 1 metre away from cut out meter tails into rcd shower circuit into mcb pirform saying fail due to main cut out fuse higher rated than rcd on shower box so says fail on choice of protective device for fault protection/overcurrent protection i know that the circuit is covered by this due to mcb however certificate says fail cos main switch is of lesser value in relation to cutout fuse
 
whilst completing certificate on pirform having installed a shower consumer unit with a 40A 30ma rcd and mcb nominal current rating of main switch in relation to overcurrent protective device (ie) main switch is rated aty a lesser value than main over current protective device, supply characteristics 100 amp bs1361

any ideas how to get round this
Stop calling it a Main Switch.

It's no different than any of the other RCDs in the installation.
 

Reply to main switch versus OPD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
996

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top