J

Jimmyb

hello, Do you need a main switch in a domestic property if there are 2 boards next to each other being fed from a service block.

I was thinking of single point of isolation for the installation but some say if there near each you dont need to.

thanks inadvance

jimmy
 
Reg 537.1.4 Tells us

" A main linked switch or linked circuit breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation."

To me 2 boards would indicate 2 installations and so there should be a switch for each board and this is normally incorporated into the CU, don't these boards have main switches??
 
I have always classed everything that is derived from the same service head and meter to be 1 installation whether there be 1 or 10 boards.
 
According to the reg Malcolm quoted, even the isolators fitted by the DNO's are not suitable ( assuming an installation is as Sintra describes) as they are only rated for isolation, not on load switching. This would cause the contacts to degrade over time.
 
as long as each CU has it's own main switch to BS 60947-3, it complies. an isolator between the meter and the CU's is purely for isolating the CUs from the supply.
 
According to the reg Malcolm quoted, even the isolators fitted by the DNO's are not suitable ( assuming an installation is as Sintra describes) as they are only rated for isolation, not on load switching. This would cause the contacts to degrade over time.

I think you'll find John that Functional switching for a BS 5419 (old type) or a BS EN 60947-3 can be achieved on load it is the on load for isolation that can not be achieved.
 
I think its a common sense issue and all the arguments for and against have been rasied by others. But you come to a point of how many points of isolation are acceptable.

I reckon if the two points are in differnt locations ie not beside each other, then you need a single isolation point. And if you have more than two even in the same location then a single isolation point should be provided.
 

Reply to Main Switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

462 excerpt below. The incoming supply is via a electrical plant room to the block of flat, each flat has a standard DNO cutout fuse but no...
Replies
9
Views
1K
  • Question
Obviously you need to check the means of earthing, Ze, and polarity no matter what for the EIC. As above, if anything looks dodgy then EICR is a...
Replies
3
Views
664

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top