Agree with that it looks like a termination issue.

Loading issue would warm up the entire cable length, although I can't tell the differential between the 100deg measurement and the cooler section behind.

Very doubtful it's harmonics causing this issue, not with this amount of loading.

Skin effect isn't that prevalent at low loading, especially with parallel cables. An you have no neutral, this is where harmonics generally become a real problem in these smaller installations.
 
Could be possible that the magnets have lost some of their magnetism? Does it run at normal temperature at lower speeds? Has the VFD frequency been changed or adjusted? Does the compressor get regular mechanical servicing?
 
That appears to be hotter where the cable terminates into the ring crimp on L3, have you tried re-terminating?
Yes we re terminated and it still existed then moved it to spare 630 a Sw beside and it still followed.
[automerge]1568492909[/automerge]
You have not lost a core on one of the parallel supply's have you
No all intact
[automerge]1568493295[/automerge]
Could be possible that the magnets have lost some of their magnetism? Does it run at normal temperature at lower speeds? Has the VFD frequency been changed or adjusted? Does the compressor get regular mechanical servicing?
The vsd varies automatically to set point on compressor but we since found a mechanical issue, the on load offload valve was faulty so compressor was flat out trying to reach a set point but dumping half it's air. Since this has been fixed the compressor is now running probably at 75 % capacity and loading on cables has reduced. Also we got a power quality audit done and I'm waiting for the report although it appears there was aprox 18% current harmonics on it . I'll let u know the outcome.
 
Last edited:

Reply to Mainswitch fuse overheating in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
423
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
924
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
883

Similar threads

  • Question
Norcal - thanks, belatedly. 'Tis the season when I don't get anything done, even though this project is near the top of the list. Per your...
Replies
7
Views
582
Well spotted, and very true Faults can have what I call a "cascade" effect, a mild fault - either a loose connection or a short, say from damaged...
    • Like
2
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top