The 17th Edition, BS 7671:2008 Corrigendum (July 2008

Clearly states joints must be accessible or alternatively use maintainance free terminals/connections. So I am going to put my money on that it does comply
No what it states is that junction boxes with screw terminals must be accessible for inspection, testing & maintenance or, alternatively, use maintenance-free terminals/connections (Regulation 526.3).
Which one of the joint methods listed in 526.3 do these Wagos, Ashleys etc. come under?
 
I think it can only be 526.3
(v) A joint forming part of the equipment complying with the appropriate product standard.

But typical to a majority of the regs a degree in legal speak is needed to interpret it.
 
No one is arguing that an enclosure is not compliant, just that the use of one is not recognised as being suitable to be inaccessible.
I don't understand what the reference to equipment complying with the appropriate product standard is about.
A consumer unit complies with the appropriate product standard, a 3 pin plug complies with the appropriate product standard, safety boots comply with the appropriate product standard.
Are any of these suitable as inaccessible joints?
 
No one is arguing that an enclosure is not compliant, just that the use of one is not recognised as being suitable to be inaccessible.
I don't understand what the reference to equipment complying with the appropriate product standard is about.
A consumer unit complies with the appropriate product standard, a 3 pin plug complies with the appropriate product standard, safety boots comply with the appropriate product standard.
Are any of these suitable as inaccessible joints?
I do have trouble doing my boots up sometimes :D
 
The screw terminals in service heads and meters for the meter tails are inaccessible. However as these items of equipment meet their relevant product standards, and the terminals are intended to be inaccessible, they meet the requirements of 526.3(v).
An item that meets the requirements of the product standard for an enclosure where the terminals are not meant to be inaccessible, does not meet the requirements of 526.3(v).
 
Last edited by a moderator:
No one is arguing that an enclosure is not compliant, just that the use of one is not recognised as being suitable to be inaccessible.
I don't understand what the reference to equipment complying with the appropriate product standard is about.
A consumer unit complies with the appropriate product standard, a 3 pin plug complies with the appropriate product standard, safety boots comply with the appropriate product standard.
Are any of these suitable as inaccessible joints?

Agreed the 536.3 (v) is ambiguous but non of your examples are "joints" therefore totally unsuitable as inaccessible joints.

The way i read it is the spring type joints used by the Ashley are part of the equipment with the appropriate product standard.
 
(vi) Equipment complying with a product standard with specific requirements to confirm that access for inspection,
testing and maintenance is not required, including for connections to the equipment made by the installer.

When the DPC came out last year there were several proposals that I highlighted to the IET. The above was a proposal to regulation 526.3 and it was a (vi) part to it. I asked if this was meant to include the WAGO type connection as an inaccessible joint, my answer was that it was still under discussion at the time of my enquiry.

I would interpret the above to include the WAGO and Ashley connections as being now inaccessible and like the rest of us await the new regulations to see if it is included.

Note The above amendment to the regulations was not copied but taken from an email I sent regarding the DPC consultation
 
Are there no joints in a Consumer Unit?
That aside, the product standard that these Ashley terminals meet the requirements of, is the one for enclosures. Where live parts are not accessible without the use of a tool.
The same product standard that JBs and adaptable boxes meet the requirements of.
Basicly the plastic part of the Ashly is acting as an enclosure.
Now if they met the requirements for BS EN 50393, which applies to low voltage cable jointing methods, then they would be suitable for inaccessinle jionts. However they don't as they're not water tight.
At present, they can only be a departure from BS7671.
 
Last edited by a moderator:
Hi All,

as promised my reply from Hager.

"Dear Lee

Thank you for your enquiry. There has indeed been much discussion! To aid installers to identify products which are truly suitable for maintenence free installation two changes to our electrical standards are coming in to place;

British Standard BS 5733 has been amended to describe the tests required to demostrate that a product is maintenance free. Products which are compliant will then be identified with an 'MF' logo.

Amendment 1 of the 17th Edition will reference this change and also describe the 'MF' mark.

Hager are happy to comfirm that our maintenence free junction boxes, J803 and J804, have always been compliant with the tests, and we are adding the MF mark to them on their lids. I notice that you are based in Dunstable. I recently attended a meeting of the NICEIC at their headquarters there, and was asked the same question that you have raised. If you are registered with them, perhaps this would be another way of satisfying yourself? We also plan to attend the Elex shows at Rugby and Sandown where we will be promoting these changes and distributing free Technical Guides and samples, so I hope we may see you at one of these.

I hope that this is of assistance

Regards
Jane"


Interesting eh!
 
The push fit terminals on the ashley junction boxes are made by WAGO and have been tested to destruction by BAE systems
thats what the guy was telling me at the wago stand at harrogate
 
Here's the latest from Hager

"Hi Lee

We havent got the new one ready to go yet, but I am sending you the original one together with our wiring accessories catalogue, which has some details of the MF mark.

I have also heard today that the ESC website is being updated on the 1st July with the following;

Q43. Can I use an electrical connector having ‘push fit’ connections that the manufacturer claims are maintenance free in an area that will be inaccessible when the installation is complete?

Not necessarily. Not all types or designs of push fit (screwless-type) clamping units comply with the requirements of Regulation 526.3 (vi).

If the connector will be inaccessible when the installation is complete, it must comply with BS 5733 for a maintenance-free accessory, be marked with the ‘MF’ symbol indicated in Regulation 526.3 (vi), and be installed in accordance with the manufacturer's instructions.

BS 5733 requires, for example, tests for resistance to ageing, cyclic loading, overload, fault current and vibration.

I hope this helps

Best wishes

Jane"

Lee
 
I have had a conversation with the ESC regarding maintainance free connectors , we know they are not as yet listed in the regs , all to change as far as the conversation goes push fit connectors will be acceptable in the new amedment but will have to be accessible unless they are marked with MF (maintainance free) this includes junction boxes and push fit connectors
 

Reply to Maintainance free JB's e.g. Ashley J803 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
814
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
988

Similar threads

How many and what type of cables do you want to join, Chocbox is the last thing I would use.
Replies
3
Views
698
Hello all easy cert users, ive been using easy cert since 2001 with no yearly subscription. and also found other people looking for older versions...
Replies
0
Views
156

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top