sivoodoo
Hi all,
Ive just installed a new split load CU, lots of old circuits in the house, every circuit works ok except one (a kitchen ring, recently installed but not by me).
The problem is this:
I conect the lives of the kitchen ring to the mcb and the earths to the earth bar, but when i touch the neutrals to the neutral bar the RCD trips.
I swapped this circuit over to the other RCD side and it happens again.
If I remove the earths of this circuit I can happily connect the neutrals with no tripping, but soon as i touch the earths to the earth bar it trips the rcd again.
Insulation resistance is good.
But there is continuity between earth and neutral on this ring.
Ive had every socket off the wall and they have been wired correctly.
What am i missing, i will be going back in the morning so any tips pointers wil be very much appreciated as Im tearing my hair out!
Thanks,
Simon.
Ive just installed a new split load CU, lots of old circuits in the house, every circuit works ok except one (a kitchen ring, recently installed but not by me).
The problem is this:
I conect the lives of the kitchen ring to the mcb and the earths to the earth bar, but when i touch the neutrals to the neutral bar the RCD trips.
I swapped this circuit over to the other RCD side and it happens again.
If I remove the earths of this circuit I can happily connect the neutrals with no tripping, but soon as i touch the earths to the earth bar it trips the rcd again.
Insulation resistance is good.
But there is continuity between earth and neutral on this ring.
Ive had every socket off the wall and they have been wired correctly.
What am i missing, i will be going back in the morning so any tips pointers wil be very much appreciated as Im tearing my hair out!
Thanks,
Simon.