Hi all,

Ive just installed a new split load CU, lots of old circuits in the house, every circuit works ok except one (a kitchen ring, recently installed but not by me).

The problem is this:
I conect the lives of the kitchen ring to the mcb and the earths to the earth bar, but when i touch the neutrals to the neutral bar the RCD trips.

I swapped this circuit over to the other RCD side and it happens again.

If I remove the earths of this circuit I can happily connect the neutrals with no tripping, but soon as i touch the earths to the earth bar it trips the rcd again.

Insulation resistance is good.
But there is continuity between earth and neutral on this ring.

Ive had every socket off the wall and they have been wired correctly.

What am i missing, i will be going back in the morning so any tips pointers wil be very much appreciated as Im tearing my hair out!

Thanks,

Simon.
 
Dont go diving into it either. Get a brew first and take it one step at a time.

Its to easy to confuse yourself and you end up going round in circles.
 
had similar.was outside socket spurred off kitchen ring. So called IP65 box cotaining extn. lead feeding garden lights and pond pump. opened box. hair dryer and resealed. end of N-E fault
 
It will more than likely be a neutral touching the KO box, I would just unscrew all easy to access sockets first and keep my fingers crossed.
 
Ok sorted it today.
i split the ring down to the last couple of single skts, disconected them tested and the problem went away, re conect the skts and everything is ok, could not see any niks in the insulation, scratched my head, wired up the CU and no problem. All good! moisture perhaps? an invisible gremlim?? god knows but now its fine??
Thanks for your replys!

Simon.
 

Reply to Major problem - am I missing something?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
725
  • Question
good thinking ps electrics i'll run with that. thanks
2 3
Replies
33
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top