Got to a customers house today after a brief discussion recently that they have brought a 2kw hob and it needs fittings. I went through the manufacturer’s instructions and they recommend it to be hard wired and that it is to be put on a 32amp breaker, obviously a 2kw appliance will pull around 8amps if my maths is correct so I am wondering am I missing something here? The hard wired part isn’t a problem, it’s more the size of breaker they recommend. There was 2x line and 2x neutral conductors too crimped together (this is where I first thought things weren’t what I am used to)
 

Attachments

  • [ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?
    4D52FC67-207A-4FBE-9E49-0DAC27F13507.jpeg
    390.1 KB · Views: 151
I'm going FCU route anyway, as I reckon it would be hard to argue a correctly fitted FCU is somehow inferior to a plug?
FCU is better than a plug for sure. But when on for sustained periods the 13A fuse, or connections, can overheat. A small box with a 13A MCB (or 16A - yes you can have a 16A MCB off a ring) and 20A DP switch off the ring would be better for sure. They could be in an adjacent cupboard.

An extreme example.

[ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?


MCB can be in a box like this. About ÂŁ3-4
[ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?
 
Last edited:

Reply to Manufacturer recommends 32amp breaker for 2kw appliance? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top