G
gpz900jim
I have been looking at the tables in my onsite guide. I have noticed that when you get to the table for radial circuits (5% drop, page 50, ) when you get to the 45amp ratings, there are maximum cable lengths given for bs1361 and bs3036 fuses, but nothing for any type of mcbs or mcbos. Does anyone know why? cheers
Thanks, any way, back to my question, does any one know why the max cable length tables in the onsite guide stop where they do? ie no max lengths for 45a breakers and no info at all for 50a breakers.?
because where do they stop? 60a 80a 100a etc etc, osg is aimed at domestic installs where 40a is typically the max anything above that youre expected to know enough to do the calc yourself.
Ok, could someone explain how to calculate the following; Max cable length for an electric shower rated at 10.5kw @ 230v using a 50a mcb, with rcd protection, and 10.mm twin and earth cable, installation method C ?
End to End resistance over
ohm resistance/ metre
10mm - 0.01 measured x 1000 = 5.46 m
10mm - 1.83, page 104 OSG
software said, 10.5kw ,230v ,50amp,
10mm clipped direct,
11.4v drop
5% drop
45.7amps current load
65.9 max cabble load
57m max cable length
hope this helps.