Hi guys, doing a rewire on my house, been a bit separation happy, and need to reduce the total load to under 80A for the incoming supply. (currently 60A but distribution coming to upgrade cutout)
House is 3bed semi, not big. under 95m2 in total. I originally designed it with
smoke alarm circuit 6A
upstairs lights 6A
Downstairs lights 6A
Ring up 32A
Ring down 32A
Kitchen ring 32A
Utility ring 32A
Cooker (7KW pre diversity) 32A
Hob (7.2KW pre diversity) 32A
Garage 20A
Shower 40A
With diversity applied to all, I end up with 156A. If I join lights upstairs with smoke alarm, up and down rings together, kitchen and utility together, reduce garage to 16A and shower to 32A, I still get 123A after applying diversity. This exceeds cons unit 100A max let alone my (soon to be)80A incoming supply.
Any thoughts? I appreciate this may be a basic question. I'm using building control at the moment and they will send an electrician to check my work at 2nd fix. I've worked with 3phase at sea for years, but houses are new to me. Thanks.....
House is 3bed semi, not big. under 95m2 in total. I originally designed it with
smoke alarm circuit 6A
upstairs lights 6A
Downstairs lights 6A
Ring up 32A
Ring down 32A
Kitchen ring 32A
Utility ring 32A
Cooker (7KW pre diversity) 32A
Hob (7.2KW pre diversity) 32A
Garage 20A
Shower 40A
With diversity applied to all, I end up with 156A. If I join lights upstairs with smoke alarm, up and down rings together, kitchen and utility together, reduce garage to 16A and shower to 32A, I still get 123A after applying diversity. This exceeds cons unit 100A max let alone my (soon to be)80A incoming supply.
Any thoughts? I appreciate this may be a basic question. I'm using building control at the moment and they will send an electrician to check my work at 2nd fix. I've worked with 3phase at sea for years, but houses are new to me. Thanks.....