Hi was called out earlier as a client has been asked by supplier to confirm KvA in order for him to downgrade meter as he feels he is paying a rate which is too high. (Dont ask me why, but if one of you guys know then please let me know too)

I had a look at supply and its a three phase supply with each phase on a 100A BS88 fuse.
the feed then runs in to a DB ( lets call it submain) which supplys DB's all around the fore court.

Submain Has:
a B32 feeding a single phase board marked Plant room,
a B40 feeding a single phase board marked 'Save LEC',
a B63 feeding a single phase board marked Pump Board,
a B63 feeding a three phase board marked DB2,
a B63 feeding a three phase board marked car wash,
a B40 feeding a three phase board marked DB3


Plant room board circuits
B6 Lights
B16 sockets
B16 lights (outside)
B20 sockets (outside)

Save LEC board circuits

B10 lights
B10 lights
B10 lights
B10 lights
B10 lights
B6 lights,

Pump board circuits,

C6 'DOMS'
B10 Contactor
B16 pumps 1,2
B16 Pumps 3,4
B16 Pumps 5,6
B16 Pumps 7,8

DB2 Circuits

B10 Alarm
B16 Cigarette machine
B16 leak detector
B16 data box
B10 Shop toilet Lights
B16 Water Heater
B32 counter Ring
C16 Vacume+air
B10 car wwash lights
B10 flood lights
B16 camera spur
B16 shop heater
B16 console heater
B16 office heater
B32 shop ring
D40 jet wash

Car wash board circuits

C40(3phase) car wash
C40(3phase) car wash

DB3 circuits

B32 (3phase) refrigerator
B16 ATM
B6 jet wash lights
B10 unknown.

As this petrol pump is operating 24 hours a day is it possible to apply diversity on these circuits,
there are places which are only used during daylight hours, there are circuits which dont get used any more, ie the car wash board is not supplying anything anymore, what I am asking really is how to go about working this out. any help or advice would be gratly appreciated.
 
You can hire from several places energy analyzers, these come with three clip together CTs and either 3 voltage connections or one voltage connection and use it to measure the power consumption over a couple of weeks and download the data to a PC.
 
how would that help in thin situation?
sorry not to sound rude, just want to figure out what you mean

The analyser will tell you exactly what KVA you will be using over a given period!! You don't need 2 weeks worth to give you the ball park figure you need, 3 or 4 days over the busiest days will give you that information...
 
thats an expensive bit ov kit aintit, the way things are these days i dont know if i'm gonna even invoice as much as that for a max demand calculation.

any way thanks for that i appreciate it, any ideas on working this out, woould i be able to apply diversity, and if so, would that be at 'sub main' or at each board.
 
I think that the client should be prepared to pay ÂŁ200 or so in order to get an accurate anaylisis of the power consumption on his site,because after you have provided the realtime readings from such a unit they could save themselves ÂŁ1000s possibly,id go for hiring the unit,it will give them all the info they need.
 
i'm just worried aboout quoting that much, as times are tough right now for everyone. i was chatting to a letting agent earlier on today, and he was complaining about the tough times too, saying how landlords don't want to spend a penny unless they absolutly have to.
I feel as we ought to look out for one and other and helping out where we can, charge a fair amount and both parties be happy. Other wise we've got the rest of the cheap unqualified guys that will do it for pennies and leave us out to dry. so i thought a calculation might be a better idea as it will save him that extra 100 pounds and make me 100 pounds and we will both be happy
 
thats an expensive bit ov kit aintit, the way things are these days i dont know if i'm gonna even invoice as much as that for a max demand calculation.

any way thanks for that i appreciate it, any ideas on working this out, woould i be able to apply diversity, and if so, would that be at 'sub main' or at each board.


The analyzer will be giving you the ''accurate'' total max KVA the installation is using ....so you can't and don't require any diversity to be applied. You connect the unit to the supply of the main DB, so it will record ''Total'' KVA of the installation.

You don't need 2 weeks of hire to give you this information, as they are hired out on weekly basis then you only need to hire for a week, so 100 quid, not 200. Well worth the cost to your client, on the savings he can potentially make immediately and in the future....
 
How experienced are you at undertaking maximum demand calculations?? If you need to ask for advice on the subject then i would think not very!! Even Engineers can get things wrong, if they don't understand the system/installation use they are applying their calculations too. I wouldn't mind betting the figure you calculate will be a lot different to what the analyzer will record as the installations max KVA requirement!!

I'm not saying that your incompetent, just that it takes a fair bit of experience to make accurate MD assessments to installations... And if you get it wrong it could cost your client a whole heap of money in this case!!!
 
Hi, The idea of that bit of kit is so that it can go round the incoming tails, live and in service with reasonable safety, you may need to connect the voltage via suitable means. One of them can take the voltage from a single 13A plug top and then takes an educated guess about the other two phases.
 
plugging it into the one phase would only give an accurate reading for that phase and as you say gives an educated guess for the other two, would that not still mean that its only a guess rather than a figure which can be more accurate using diversity.
 
Hi, The idea of that bit of kit is so that it can go round the incoming tails, live and in service with reasonable safety, you may need to connect the voltage via suitable means. One of them can take the voltage from a single 13A plug top and then takes an educated guess about the other two phases.

No need for any educated guesses here, the analysers of today do the calculations for you on 3 phase supplies where only one phase voltage is being monitored.
 
Thats the thing engineer54, when its not monitoring the other two phases surely its taking a guess at whaat they are doing, therefore an educated guess. How else is it possible for it to give me information which it hasn't even been plugged into.
 

Reply to max demand at petrol pump in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top