HI Guys
I have a 8 flats and 2 retail units due to be built soon and i am trying to work out the Maximum demand for each of the flats and the 2 shops so the supplier can ensure a large enough mains supply.
The Retail units are to just have a supply to a distribution board, the shop is not too large and without any definite future spec given to me i would assume a 16mm 4c SWA 3P+N would be adequate.
The flats are of differing sizes but i have done the calcs and worked out the correct sizings for the space to be heated.
If i allow diversity for the final circuits and taking the storage heating at 100% the total max demand is between 123A and 164A! In every property ive been in storage heaters are fed from the same supply as the Consumer Unit but via a timeswitch thereby still using the one EP fuse 60A-100A.
Would the flats require 2 feeds or could this still be achieved with the 1 supply as the storage heating would not come on untill midnight?
I have a 8 flats and 2 retail units due to be built soon and i am trying to work out the Maximum demand for each of the flats and the 2 shops so the supplier can ensure a large enough mains supply.
The Retail units are to just have a supply to a distribution board, the shop is not too large and without any definite future spec given to me i would assume a 16mm 4c SWA 3P+N would be adequate.
The flats are of differing sizes but i have done the calcs and worked out the correct sizings for the space to be heated.
If i allow diversity for the final circuits and taking the storage heating at 100% the total max demand is between 123A and 164A! In every property ive been in storage heaters are fed from the same supply as the Consumer Unit but via a timeswitch thereby still using the one EP fuse 60A-100A.
Would the flats require 2 feeds or could this still be achieved with the 1 supply as the storage heating would not come on untill midnight?