Max Demand calc for new supply | on ElectriciansForums
Discuss Max Demand calc for new supply in the Australia area at ElectriciansForums.net
L
leestaf
HI Guys
I have a 8 flats and 2 retail units due to be built soon and i am trying to work out the Maximum demand for each of the flats and the 2 shops so the supplier can ensure a large enough mains supply.
The Retail units are to just have a supply to a distribution board, the shop is not too large and without any definite future spec given to me i would assume a 16mm 4c SWA 3P+N would be adequate.
The flats are of differing sizes but i have done the calcs and worked out the correct sizings for the space to be heated.
If i allow diversity for the final circuits and taking the storage heating at 100% the total max demand is between 123A and 164A! In every property ive been in storage heaters are fed from the same supply as the Consumer Unit but via a timeswitch thereby still using the one EP fuse 60A-100A.
Would the flats require 2 feeds or could this still be achieved with the 1 supply as the storage heating would not come on untill midnight?
To be honest I have yet to see an economy 7 installation and normal installation having separate supplies. 99% would be as you described either utilizing a time clock, or as now we have a dual meter, with the one 240/230 supply.
You may find that it would be 80-100amp rather than a 60amp which most flats would utilize quite easily. No I doubt very much you need 2 supplies unless there are other high load demands on the installation
Thanks Malcolm
I was planning on using a 25mm SWA 100A supply with a dual E7 meter at the meter cupboard thereby using only a single supply, a timeclock at the CU controlling a contactor for the heaters.
Reply to Max Demand calc for new supply in the Australia area at ElectriciansForums.net
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...