This may sound abit dumb, But looking at a small office with new install of dado trunking 7 sockets, only supplying 3 desktop pc's 3 LCD monitors and a 36 inch LCD Monitor, these running might be odd mobile or laptop plugged in now and then. what i was concerned was that is run off a RAdial 2.5mm T&E on 16amp breaker. If I done the x by 0.4 trick would be fine and within the be ok as far as demands, but im thinking there is still too much for this circuit. what diversity would i apply? i SEEM TO HAVE LOST A BRAIN.
thinking (this approx) 3 desktops are max 250w each LCD small ones 75w each and 36"150w.
would come out nearing 5amps
but if i apply the 100% of largest point plus 40% of every other point, we are sky high..
any takers?
thinking (this approx) 3 desktops are max 250w each LCD small ones 75w each and 36"150w.
would come out nearing 5amps
but if i apply the 100% of largest point plus 40% of every other point, we are sky high..
any takers?