Hi, just wondering if im doing this right...
fitted a new board in my house, is this right for diversity?
Shower 40A 7.5KW - 32A
Sockets 32A 100% - 32A
Sockets 16A 40% - 6.4A
Boiler 16A 100% 3A (3A fuse in spur, or do i use 16A?)
Smoke 6A No Diversity 6A?
Lights 6A 66% - 3.96A
Lights 6A 66% - 3.92 A
Total - 87.32A
do i use 40% of total 34A?
been a few years since i done this at college!
thanks.
As a rule of thumb, add up all but the largest circuit breakers, multiply by 0.4 then add on the largest.
So.....(32+16+16+6+6+6) x 0.4 + 40 = 72.8A
Thanks for that JUD, bit of a problem as there is only a 60A main fuse,
i know the house wont use more than that in reality but whats the correct way to go about it? have it upgraded to 80A?
cheers
Reply to Max Demand in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
    • Friendly
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Haha yes, it is. Must be a northern expression. Have a Google 😂