When doing pirs and pirs before consumer unit changes or db,s when calculating the max demand with help from OSG i often find installations max demand well exceeds the cut out fuse. customers dont care what do yous guys do about it
 
i use a rule of thumb. add up the MCB ratings and divide by 2. or, you could calculate more accurately applying diversity.
 
Don't forget that as a competent person having knowledge of the working installation, you can use your own methods to calculate a truer reflection of maximum demand.

The written figures and percentages are more suited to design calculations.
 
It is often the case that the calculated maximum demand exceeds the rating of the cut out fuse.
Many have been in use without any problems for many years.
To be honest, I can't actually recall ever having a domestic installation where the cut out fuse has blown.
Had it on industrial installations quite a few times, but that can sometimes be down to unbalenced 3 phase supply voltages.
 
We done a pir the other day in a house 60 amp bs88 fuse supplying the following mcb,s 4 x b32 , 1 x b40, 2 x b16 ,4 x b6

There you have it, it's not an exact science and as spinlondon points out, you just don't see a service fuse blown on overload.
 
I use the following calculation. add up the rating of all the circuit protective devices, and times the value by 0.4. This is near enough to be acceptable, and is quicker than applying diversity. Done this for years with no problems.

Cheers..........Howard
 
I use the following calculation. add up the rating of all the circuit protective devices, and times the value by 0.4. This is near enough to be acceptable, and is quicker than applying diversity. Done this for years with no problems.

Cheers..........Howard


I multiply by 0.42 but only on the 3rd Tuesday of a month and never in an Easterly wind ;)
 

Reply to Max Demand in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
602

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top