Are you sure it is 20mA and not 30mA
Most sites I've done will be TT and have an upfront 100mA RCD and then a CU with sockets on a 30mA and depending how the lights are installed they will have just a mcb supported by the upfront 100mA. Have a good look at sections 704 and 411.8 for reduced low voltages in the BS 7671-2208. Table 41.6 will give you the Zs times for the lights, but I'm sure they will be on some sort of RCD.
The 30mA and the 100mA will be 300mS @ x 1 and 40ms @ x5 if the system is TT then the X 2 for them is150mS maximum well within the 0.2 wanted.
If you using a time delayed 100mA then the times @ x 1 will be 130min/500max mS and @ x 5 will be 40min/150max mS