Hi their does anyone now were i can get maximum earth fault loop impedance for a BS88 400A fuse with a disconection time of 5 secs cheers danny
A book by Trevor E Marks published in 1999, A Hanbook for compliance has time curves for a 400A BS88 fuse.
400A 5 seconds = approx 3000A
Hot value
Zs = Uo/Ia = 230/3000 = 0•076ohms
Cold value
0•076 x 0•8 = 0•06ohms
cheers guys ended up ringing the manufacturer of the fuse as recommended by the niceic which was cooper bussman and they quoted 0.9 ohms thanks for the reply that links spot on:D
Reply to Max Earth Fault loop impeadances for400A bs88 5 secs in the Electrician Talk | All Countries area at ElectriciansForums.net
It's the same with any system, if you put poo in, you get poo out!
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.