boballum

How about this for a ponder.....
Lighting circuit wired in metal conduit buried in concrete, conduit used as the earth no seperate CPC

Replaced board reconnected conduit to main earth but readings are 45ohms obviously the conduit has broked down

My question is this, before RCD's on lighting circuits we would have rewired it but now it has an RCD with a max permissable loop of 1551ohms (roughly!) is this reading acceptable????

The circuit has class 1&2 equipment on it
 
The metal conduit is still an exposed conductive part containing live conductors and has therefore still to be properly constructed and provide good continuity throughout it's run and be earthed.
 
I agree, obviously it's not what you or the customer want to hear, but it does want sorting.

I hate that part of the job, breaking bad news to customers, you worry that they will think you're trying it on, but at the end of the day you have got to cover your arse!
 

Reply to Max loop reading using RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
767
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top