Hi,
In the OSG it states that for tables 2A-2C the max earth fault loop impedances are for circuits with a copper protective conductor.(P99 note 1)
What then would the appropriate allowed reading be for say a 2-core SWA cable using the SWA for a protective conductor (which I think is allowed)
I,ve probably missed something, please help !
Thanks in advance.
 
ITs the protective device which will give you the max Zs IE: BSEN60898 B type with a 0.4 second disconnection time 32 amp = 1.44 , 16 amp = 2.87 ,6 amp = 7.66 etc
 
Last edited by a moderator:
Thanks for the quick reply Nick, I,ve not explained my question very well, I understand that the protective device determines the max ZS via the tables but my reading of the OSG(probably wrongly) is that these values are for circuits with a COPPER protective conductor not SWA ?
Help the feeble minded
 
The tables in the OSG are for when the ambient temperature is at 10°C, and the tables take into account the difference in resistance of the conductors between that ambient temperature and the conductor operating temperature of 70°C. Thes particular tables are only of use when the CPCs are copper.
If you want to determine the effectiveness of the SWA as a CPC, you should use the adiabatic equation and the values of K quoted in BS7671, and then adust for ambient temperature to give the maximum acceptable measured value.
 
It doesnt matter what cable type it is , although the cpc size does play a part in it but itsa tables 41.2 to 41.6 that will determin the Zs ,if the Zs reading exceed the permitted levels then 2 options to over come this is to increase the size of the CPC or install an RCD , if on an SWA cable the armour is not large enough to comply with the regulations , you either install
a seperate earth or use a 3 or 5 core CWA depending whether its single or three phase hope this helps
 

Reply to Max permissible ZS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top