If suggest higher than 10ka rated mcbs if the pfc was measured at 10ka.
Was a minimum suggestion as he said 10k not higher.... as its domestic most common brands are 6k or 10k ratings ....if he had said 11k 12k etc then yes i would obviously have suggested mcb's for such but its only a recommendation as he's not required to fit them anyway.
 
Darkwood I know you know that, I was just pointed it out to those who are still green.

E54 think the company paid £400 is for it maybe a little less. It's an alright peice of kit, pfc in our subs are 15~35ka dependent on the tx feeding them obviously.
 
Darkwood I know you know that, I was just pointed it out to those who are still green.

E54 think the company paid £400 is for it maybe a little less. It's an alright peice of kit, pfc in our subs are 15~35ka dependent on the tx feeding them obviously.


That's a pretty good price, i'm sure on the last project, a comparable tester was over the £500 mark!!
 
Most DNO's, if asked (by enquiry) would say 16kA is the max PFC available on a single phase 100A or less supply.

I don't for one minute believe the Op's supply is any where near the levels of PFC his meter's are indicating, due to inaccuracies and method of measurement, as many posters here have already pointed out.

Typically EFLI meters measure the volt drop in mV at a measurement of around 20-25A load, and at close to the TX is at the lower end of the instruments capabilities (check the accuracy figures quoted in the user manual).
Under actual kA fault levels it is doubtful the TX could even supply the installation at that level of fault current before the cut fuse failed

The OP would either need a more accurate meter, or use IQ's method of measurement, as any slight discrepancy in the loop reading has a massive bearing on the PFC reading.

When you consider the DNO's supply cable has some resistance, as well as the cut out fuse and the meter itself as well the tails, then the calculations don't really add up, as the fuse, the Dno's cable, the meter and the tails would need a total resistance of 0.001 ohms for a PFC of 23kA single phase calculated @ 230V
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Southend on sea ESSEX

Thread Information

Title
Max PFC gone through the roof....Ideas anyone?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
46

Thread Tags

Advert

Thread statistics

Created
Eggster71,
Last reply from
spark 68,
Replies
46
Views
6,195

Advert

Back
Top