Hypothetical situation, power supplied from a generator - So a temporary installation.
BS 61009 Type C 100mA RCBO – 32A fitted at generator
Cable run is approx. 300m, in 4mm HO7 Rubber PVC flexible cable ran outdoors, terminated in a 32A socket (single phase)
Ze = 0.03 ohm
Maximum Zs is 0.72 ohm
Calculated Zs is 1.89 (0.03 + 1.86)
If a distribution box is fitted at the end of a cable run, with 4 x 16A sockets wired so there are 2 16A Type C RCBO's, each feeding 2 x 16A Sockets would this offer enough protection as the Zs has been exceeded.
Load on the cable is approx 6.5A, so does exceed the max voltage drop.
I know this isn't ideal, and the cable run should either be shorter, or wired in a bigger size cable. But it's a weird situation.