M
Merl
Can anyone put my mind straight on the Max Zs value for a 32A type 'C' BS61009. The BRB states the max measured value for this type of breaker as 0.72 ohms. Using the rule of thumb ( x 0.8 ) this brings the value to 0.57 ohms. Is this 0.57 ohm maximum measured value to meet the 0.4 & 5 second disconnection times in a short circuit fault conditon? Am I right in thinking that any measured value above this 0.57 ohms the breaker wouldn't trip within the required times??
The reason I'm asking is, I've just done some testing and the sockets are protected by 32A type 'C' RCBO's and a number of Zs test readings are above the 0.57 ohm maximum permitted value, but would be below the max permitted value of a type 'B' RCBO and well below the 1667 ohms for earth fault protection.
Any advice would be appreciated!
Cheers!
The reason I'm asking is, I've just done some testing and the sockets are protected by 32A type 'C' RCBO's and a number of Zs test readings are above the 0.57 ohm maximum permitted value, but would be below the max permitted value of a type 'B' RCBO and well below the 1667 ohms for earth fault protection.