Dan007
London
Please can people clarify what value they insert in the Max Zs field on certification.
I've always input 100%. Currently in disagreement with another person as they are specifying 80%.
Done my 2391 in 2008 and I was taught and told it's always 100% and it's down to the QS to interpret the results and ensure they fall with 80% allowing for correction factors.
Third argument is that in GN3 and OSG they specifically state 80% - however I always understood these to be quick reference pocket guides while on site.
In the mentioned publications and BBB the model forms show 100% in the compelte fields for examples. Secondly the small print at the bottom makes reference to the Publication and values in Chapter 41 aka BBB and 100% values.
Your thoughts please people
Hummm. Horses and courses n all that. I'd complete the field as required and complete the 30mA section so the certificate detailed the correct OCPD and associated Max Zs and/or RCD type.
Can anyone shed any light on this? Have they had this discussion with their area engineer?
I’m not sure why you would need the discussion with your area engineer? What value would you record on the schedule if it was TT....The max Zs value of the OCPD or the max Zs permitted for the RCD that’s providing the earth fault protection? It’s clear to me what you should be doing.
I do not need to speak to my NICEIC Engineer. I understand what is required.
How else would you meet disconnection times if the Zs is too high?
Is there an excerpt from BS7671 that details this (Use of max RCD values) over the Max Zs of the OCPD when considering Zs values that exceed the 80% factor?
To be honest the use of an RCD to cover fault protection on a TN system is not ‘textbook’. But sometimes you need to think outside the box. There are otherways to combat this issue, which is only an issue due yo poor design but it is completly unrealistic to rewire a circuit due to high measured Zs when an RCD will provide protection and still meet 7671.
Absolutely! Couldnt agree more. But is there an excerpt for stating one value over the other? Or is this just an understanding you have with your engineer. I'll definitely raise this with mine tomorrow if thats what you guys/girls are doing and its deemed acceptable.
I don’t run anything by my engineer.
You used the value of whatever the OCPD is that you are using.
What the foot note on the model form says is...
"Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in chapter 41 of this standard, state the source of the data in the appropriate cell for the circuit in the 'Remarks' column (column 25) of the schedule"
So it doesn't state you must record the 100% value, only that if it isn't from BS 7671 that you state where you got it from.
But must comply with 7671.
Yeah, but I've just looked and I can't find anything in the regs that stipulates you record the 100% value. Just that footnote which stipulates if it's not from BS 7671 you state where it is from.
If you multiply a value from the tables by 80%, the source of the value is still the standard.
I said earlier I record 80%... I do because it's the default in NAPIT Desktop which I use for doing EICs and EICRs, you can change it, but the cert then includes markup to show whether it's the 100% value or the 80% value.
It's how I was taught when I did C+G 2932, 2394 and 2395 a couple of years ago.
Reply to Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net