Bromley, Kent
Hi All,
Thank you for welcoming to this forums
I just want to clarify that the Value I need to enter 100% or 80% in the last column "Maximum Zs Permitted by BS7671"
is it 80% from the table 41.3 from 18th Edition Regs - Page 62 or the value from Pocket Guide 18
Thank you
Loges
  • Pocket-Guide-18.pdf
I was taught to put the 80% down. And that’s what I’ve always done.
This was discussed in a previous thread and some said 100% others 80%.
I don’t think it really matters as long as you know which your using on the comparison to the actual Zs read and you know what your doing.
As Strima says, you put down the value found in BS7671.
This is so the customer gets confused when the measured value is less but it still fails.
but then you confuse them even more by telling them it's oK, with RCD it's 1667.
BUT 80% is not max. it's corrected assuming cable will be fully loaded and at 70 deg.C. this will never happen. cables will be at least 30% overloaded and breaker will trip long before that temp. is reached (assuming circuit has been designed in compliance with 7671). tin hat on.
Absolutely agree. I don’t understand why we even use 80%. It is overkill.
I think 90-95% would be adequate just to allow for design flaws and anomalies.
However the Cmin factor that gives 95%. So I recon that should be sufficient.
Obviously there may be very good reasons 80% is used. Maybe a figure plucked out of the air. I don’t know. Any ideas?
Reply to Max Zs Permitted by BS7671 value in the UK Electrical Forum area at ElectriciansForums.net
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...