Does anyone know how to find the max ZS for these types of breakers? Thanks in advance guys.
 

Attachments

  • [ElectriciansForums.net] Max ZS
    F4B05F9E-7328-4D28-8507-ED7556F85A75.jpeg
    295.4 KB · Views: 43
That's a motor protection breaker and they normally provide overcurrent and short circuit protection I could be wrong here but Zs values aren't applicable as fault protection is provided elsewhere.
 
Does anyone know how to find the max ZS for these types of breakers? Thanks in advance guys.
You do know they are motor protection devices not standard mcbs

It uses type 2 coordination between the starter and inbuilt magnetic trip.

The magnetic trip is 13x the maximum setting.

So if you have a 10A this would be 130A even if the actual motor current was set to say 8.3A.

Given 130A, the voltage and the standard correction factors, you can calculate the Zs

EDIT

seen the type of device has just been mentioned- x post!

These devices have inbuilt thermal characteristics targeted at motor protection rather than standard curves, and a direct magnetic trip, for overloads the curve trips the starter, but for large fault current the inbuilt breaker breaks the fault - this is type 2 coordination.

It's an Alan Bradley device BTW.
 

Reply to Max ZS in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
706
  • Question
A lot will depend on the load on the tray / basket / trunking and the span before it bends / distorts
Replies
2
Views
541

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top