Hi can you put me straight on this.
When testing a new installation your measured Zs must be less than 80% of regs figure, allowing for temperature difference at testing and normal operating.
So when doing a periodic, as this installation is already at normal operating temperature, your measured Zs must be less than 100% of regs figure?
sorry if im being blonde here
 
Forgive me if I misunderstand your post, but I think you are getting confused between ambient temperature, and conductor operating temperature under fault conditions.

Under fault conditions conductor temp will rise considerably thus increasing the resistance of the conductor.
When testing Zs your meter will not replicate the rise in temperature and thus the increased resistance/Zs. That is why we only go to 80% of max Zs values in the BRB.

It makes no difference whether the installation is new or old. Max measured Zs must always be 80% or less than max values in the BRB.

Hope this helps
 

Reply to max Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K
so Ze 0.35Ohms and my Part of the Circuit just half of R1+R2 is 0.19353Ohms as its 1.5mm x 10m so well under but dont know of any switch gear...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top