Hello all,
Im not an electrician or really have much background in electrical theory but I was Just wondering if someone could show me how I would go about answering the following question.

A power ring is to be installed using a 2.5mm twin and earth PVC cable. The circuit will be protected by a 32A type B circuit breaker. The cable will be directly clipped to the walls and joists. Calculate the maximum cable run for the ring if the external earth loop impredance is 0.8Ω?

Take into account electrical resistances for 2.5mm and 1.5mm copper cables are 7.41 mΩ/m and 12.1 mΩ/m. The maximum earth loop impedaqnce for a type B circuit breaker is 1.44Ω and the correction factor for PVC cable is 1.2.

Thank you for your help,

Luke

 
I'll be honest im a mathematics student doing a module on basic electrical theory and I dont understand how to complete this problem.
 
Hello all,

A power ring is to be installed using a 2.5mm twin and earth PVC cable. The circuit will be protected by a 32A type B circuit breaker. The cable will be directly clipped to the walls and joists.

Calculate the maximum cable run for the ring if the external earth loop impredance is 0.8Ω?

Take into account electrical resistances for 2.5mm 7.41 mΩ/m
and 1.5mm copper cables 12.1 mΩ/m.
The maximum earth loop impedaqnce for a type B circuit breaker is 1.44Ω and the correction factor for PVC cable is 1.2.


Total resistance of the loop (from line to earth) of twin and earth cable plus the external loop impedance must be less than or equal to the earth loop impedance for the breaker (as corrected).

You have the resistance of the cables and with a ring final circuit there will be two cables of equal length both sharing the current.
resistance of resistors in parallel is 1/R = 1/R1+1/R2+1/R3+1/R4....

Take external loop impedance off the corrected max ELI and the remaining resistance is the maximum allowed for the cables.
Back calculate to obtain the maximum length of the cable permitted.
 
OK, start with the formula Zs(max.) = Ze + (R1+R2), where R1 is the resistance of the L. and R2 that of the E.
 
Thank you.

Maybe an even easier one first;

The turbine for the system will provide a maximum voltage of 200V DC to the inverter at a current of 5A. The specification of the inverter shows the input voltage must not fall below 170V else the inverter will shut down. Calculate the maximum run that can be used if 2.5mm[SUP]2[/SUP] cable with a loss of 19mV / A / m is installed to connect the turbine to the inverter.

Would this simply be;

0.019 x 30 = 0.57
0.57 x 5 = 2.85
30/2.85 = 10.53m​
 
Thank you.

Maybe an even easier one first;

The turbine for the system will provide a maximum voltage of 200V DC to the inverter at a current of 5A. The specification of the inverter shows the input voltage must not fall below 170V else the inverter will shut down. Calculate the maximum run that can be used if 2.5mm[SUP]2[/SUP] cable with a loss of 19mV / A / m is installed to connect the turbine to the inverter.

Would this simply be;

0.019 x 30 = 0.57
0.57 x 5 = 2.85
30/2.85 = 10.53m


No.
volt drop = 19mv/A/m
you're allowed 30 volts @ 5A
so......
 
You have a current running of 5A so if you calculate the value of volts dropped for a current of 5A over one meter.
Then you are allowed a maximum of 30V drop do the division and you will get the number of metres permitted.
 

Reply to Maximum Cable Run Question. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Suggests yes, but doesn't prove it, not all imperial cables were tinned.
2
Replies
15
Views
1K
davesparks
D
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top