Hello all
I've got my NICEIC inspection in about 8 weeks time so i can hopefully join up with the NICEIC if all goes to plan.
For the major im doing a consumer unit change at my mum and dads house ive spoke to western power they are coming out soon to fit an isolator in the line so i can safely isolate the incoming tails from the supply.
Now this is not a new installation but im still working out all my demand and diversity for each of the circuits.
I would appreciate a little guideance or help from the fellow electricians on here thanks.
The list so far
Lighting circuit downstairs
1250watt is total wattage of all lights downstairs
1250/230 = 5.43amps then i have to add 66% of total current demand
5.43 x 0.66 = 3.58amps
cable selection
1.0mm carrys 16 amp 1.5mm carrys 20amp clipped direct even in worse case scenario ref methods both of these cables will be ok
MCB type B 6amp
Lighting circuit upstairs
620 watt is total wattage of all lights upstairs
620/230 = 2.6amps then i add 66% of total current demand
2.6 x 0.66 = 1.7 amps
Cable selection
1.0mm carrys 16amp 1.5mm carrys 20amp clipped direct even in worst case scenario ref methods both of these cables will be ok
MCB type B 6amp
Cooker and Hob built in
10.7kw
10700 / 230 = 46.5amps
46.5 - 10amps = 36.5amps
36.5 x 0.3 = 10.95amps
10.95 plus the 10 amp we took off 10.95 + 10 = 20.95
+ 5 amps as the cooker switch has a socket incorporated = 25.95 amps
MCB 32amp type B
cable 6mm or 10mm to supply the cooker
immersion heater
3kw
3000 / 230 = 13amps
MCB 16amp type B
cable 1.5mm or 2.5mm
Ring circuit downstairs
7000 watts total
7000 / 230 = 28.7amps this is where im not to sure in OSG it says 100% of current demand of largest circuit + 40% of current demand of every other circuit
so is this correct
28.7 amps round up to 29
29 x 0.4 = 11.6amps
29 + 11.6 = 40.6amps ?
or is it
32 amp for mcb
32 x 0.4 = 12.8
32 + 12.8 = 44.8amps ?
if so seems as though its a ring its unliklely all sockets and appliances will be on downstairs all at the same time so a 32 amp MCB would be ok ?
any help or understanding on this would be great many thanks.
I've got my NICEIC inspection in about 8 weeks time so i can hopefully join up with the NICEIC if all goes to plan.
For the major im doing a consumer unit change at my mum and dads house ive spoke to western power they are coming out soon to fit an isolator in the line so i can safely isolate the incoming tails from the supply.
Now this is not a new installation but im still working out all my demand and diversity for each of the circuits.
I would appreciate a little guideance or help from the fellow electricians on here thanks.
The list so far
Lighting circuit downstairs
1250watt is total wattage of all lights downstairs
1250/230 = 5.43amps then i have to add 66% of total current demand
5.43 x 0.66 = 3.58amps
cable selection
1.0mm carrys 16 amp 1.5mm carrys 20amp clipped direct even in worse case scenario ref methods both of these cables will be ok
MCB type B 6amp
Lighting circuit upstairs
620 watt is total wattage of all lights upstairs
620/230 = 2.6amps then i add 66% of total current demand
2.6 x 0.66 = 1.7 amps
Cable selection
1.0mm carrys 16amp 1.5mm carrys 20amp clipped direct even in worst case scenario ref methods both of these cables will be ok
MCB type B 6amp
Cooker and Hob built in
10.7kw
10700 / 230 = 46.5amps
46.5 - 10amps = 36.5amps
36.5 x 0.3 = 10.95amps
10.95 plus the 10 amp we took off 10.95 + 10 = 20.95
+ 5 amps as the cooker switch has a socket incorporated = 25.95 amps
MCB 32amp type B
cable 6mm or 10mm to supply the cooker
immersion heater
3kw
3000 / 230 = 13amps
MCB 16amp type B
cable 1.5mm or 2.5mm
Ring circuit downstairs
7000 watts total
7000 / 230 = 28.7amps this is where im not to sure in OSG it says 100% of current demand of largest circuit + 40% of current demand of every other circuit
so is this correct
28.7 amps round up to 29
29 x 0.4 = 11.6amps
29 + 11.6 = 40.6amps ?
or is it
32 amp for mcb
32 x 0.4 = 12.8
32 + 12.8 = 44.8amps ?
if so seems as though its a ring its unliklely all sockets and appliances will be on downstairs all at the same time so a 32 amp MCB would be ok ?
any help or understanding on this would be great many thanks.