hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity again ?

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.
 
hi,
using table 1B app 1 OSG

ring main (30a) no diversity = 30A. My interpretation is 100% of the biggest point of utilisation which can only be 13A then 40% of every other point which would be (30-13)*.4=6.8A. Therefore diversity = 19.8A)
cooker unit(30a) 10A+30%(fl)+5A =24A. It's actually slightly less than this - it's 30% of anything over 10% which is 20A. Therefore diversity (20*.3)+10+5= 21A or 5A less if you don't have a socket outlet)
shower(40a) no diversity = 36.9A. Agree
radial(20a) 40% = 8A. I make it 13A+30% of 7= 15.1A
radial(20a) 40% = 8A. I make it 13A+30% of 7= 15.1A
lights 66% =3.04A. I make it (700/230) * .666 = 2.02A

Total diversity = 109.92A

Note though that on page 95 of the OSG it states, 'the values given in Table 1B, may be increased or decreased as decided by the installation designer concerned' as the 'values given in the Appendix are intended only for guidance...'
 
Last edited by a moderator:
[ElectriciansForums.net] maximum Demand/ DiversityJust somthing in one of my books
 

Reply to maximum Demand/ Diversity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top