daveb1
looking to get a bit of help got a job that currently has 8 flats and a landlord supply and a big office on the ground and basement
After using the OSG for diversity have come up with the following
118A per flat (no gas)
127A for landlord (lift etc)
180A for office (air con)
118x8=944+127+180=1251AMPS this seems way to much i know! but would rather cover myself so when the office are giving these to the supply company they are asking for kva?
At the moment they have a 200A 3 phase supply
The developers are looking to change the office into 3 more flats so 3X118=354amps more
so with the office gone we are looking at a total of 1425Amps (sounds like its getting confusing)
so my question is how can i get a kva value for the supply company? with 1425A 3 phase
Any help would be appreciated Thanks Dave