waynelester

hi,i have completed a consumer change but feel that the total demand as calculated is greater than supplier fuse (60AMP).the property has had numerous extentions.what would you put on eic and would you make a note of concerns in existing installation and recomend upgrade, any comments appreciated,thanks
 
hi,i have completed a consumer change but feel that the total demand as calculated is greater than supplier fuse (60AMP).the property has had numerous extentions.what would you put on eic and would you make a note of concerns in existing installation and recomend upgrade, any comments appreciated,thanks

Well what was the calculated maximum demand?
 
hi if calculating using standard formulae based on breakers 90amp

Is 'the standard formula' disregard the largest device, add up the rest and multiply by 0.4 on a full moon with a prevailing North wind? :)

It's down to your judgement as a competent person to decide whether there is actually a problem here, you are free to use other methods to calculate maximum demand based on your knowledge of that particular installation.

If you're still concerned, you can call the DNO on behalf of the client and check out available options.

As always, a note on the EIC mentioning that 'maximum demand is approaching the rating of the supply fuse' shows that you have considered the situation.
 

Reply to Maximum demand in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
289
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
822

Similar threads

Max demand can normally be pulled from the meter on existing installations for commercial/industrial meters, cycle through the readings- its...
Replies
9
Views
2K
  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
400

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top