Table 41.3 gives the maximum earth loop impedance on a type B 32a breaker to 60898 as 1.44 ohms, the testing schedule on the domestic cert asks maximum permissble loop impedance, in the test and inspect notes I seem to remember that you are required to write the full 1.44 but I'm sure that you allow for 80% due to fault condition temprature?? bringing it down to 1.15. Answers on a virtual postcard please